Keep in mind, per the 2008 NEC, Article 600.7, (B)Bonding, (1) bonding of Metal parts, metal parts and equipment shall be bonded together.....and shall meet the requirements of 250.90. Also, under 600.24, Class 2 Power Sources, (B)Grounding, metal parts of signs and outline lighting systems shall be bonded and grounded in accordance with 600.7.
This is an NEC requirement, not solely a UL requirement. also, a majority of municipalities run one to two code cycles behind the current so if the 2011 code remeoves this requirement, it may still be in force at the local level. Additionally, the AHJ has the right to supercede the requirements of the NEC. From my perspective, the simplest thing to do is provide bonding conductors and include installation instructions for your sub contract installers. Pretty low-cost insurance against a red tag, if you ask me.